veritas
Electrical
- Oct 30, 2003
- 467
I saw in a text on the subject recently that the neutral earthing resistor (NER) on the secondary side of the neutral earthing transformer (in the neutral of a generator)reflected to the primary should be around the same magnitude as the generator capacitance to earth.
In my application, the NET = 20kV to 415V, NER = 0.9ohms leading to an "effective" primary impedance of 2.1kohm.
My question is
1. why does the "effective" R have to match the capacitive impedance?
2. What exactly is meant by the generator capacitive impedance? Is it the value of Xc to ground per phase?
Thanks.