arozman
Electrical
- Aug 20, 2003
- 1
We have following single pole schematics: 10.5 kV, 88MVA, 22% generator (grounded via resistors) is connected to step-up transformer (90MVA, 117/10.5 kV, YNd5, 11%) via bus bar connection. Between generator and transformer the generator circuit breaker and two feeders (for static excitation system and auxilliary power supply, 1MVA each) are located; excitation feeder is on generator side of circuit breaker, auxilliary power supply feeder is on transformer side of breaker. Transformer is connected to OHL via another (110 kV) breaker.
We shall utilize own differential protections for both machines: 87G for generator and 87 T for transformer.
Is it suitable to add the third differential protection, which should cover area between generator neutral and low voltage side of step-up transformer (including excitation feedder, generator circuit breaker, auxilliary power supply feeder)?
THANK YOU!!!
We shall utilize own differential protections for both machines: 87G for generator and 87 T for transformer.
Is it suitable to add the third differential protection, which should cover area between generator neutral and low voltage side of step-up transformer (including excitation feedder, generator circuit breaker, auxilliary power supply feeder)?
THANK YOU!!!