andross
Electrical
- Feb 3, 2005
- 13
Hi,
We have a 11kV generator, which is capable of running in parallel or as an island. It is directly coupled to an 11kV switchboard (through a CB) The generator neutral has an automatic isolator for disconnection from earth when running in parallel with utility. The 11kV switchboard has its own earth electrode. Do we have to provide a separate (and segregated from the switchboard electrode) electrode for the generator neutral, or can it be connected to the 11kV electrode?
We have a 11kV generator, which is capable of running in parallel or as an island. It is directly coupled to an 11kV switchboard (through a CB) The generator neutral has an automatic isolator for disconnection from earth when running in parallel with utility. The 11kV switchboard has its own earth electrode. Do we have to provide a separate (and segregated from the switchboard electrode) electrode for the generator neutral, or can it be connected to the 11kV electrode?