veritas
Electrical
- Oct 30, 2003
- 467
In the diagram gen is high impedance earthed with the EF current limited to 10A (sorry, not shown on SLD).
I have a concern regarding EF protection on a steam turbine generator system as per the attached. For an EF at F1, the generator EF relay trips in 0.5s. This leads to a turbine trip, which in turn leads to a reverse power condition which in turn leads to a GCB and field CB trip. Thus it could be several seconds before the GCB trips. The fault is now on an ungrounded system. There is a neutral overvoltage relay fed from a broken delta VT secondary as shown. Trip time is 3s.
Question – is it necessary to have a 3s delay? There is nothing else to grade with. Gen trfr is sometimes back energised via the Aux trfrs. Would that be an issue?
I am concerned that the 23kV bus, two auxiliary trfrs and the gen trfrs are subjected to the voltage rise on the healthy phases longer than what is necessary. Danger is that fault could lead to another flashover which will be much more severe. Another concern is arcing faults with unearthed systems and the transient overvoltages.
Are my concerns valid or is 3s okay? Any other dangers? I was thinking of bringing it down to 0.1s.
I have a concern regarding EF protection on a steam turbine generator system as per the attached. For an EF at F1, the generator EF relay trips in 0.5s. This leads to a turbine trip, which in turn leads to a reverse power condition which in turn leads to a GCB and field CB trip. Thus it could be several seconds before the GCB trips. The fault is now on an ungrounded system. There is a neutral overvoltage relay fed from a broken delta VT secondary as shown. Trip time is 3s.
Question – is it necessary to have a 3s delay? There is nothing else to grade with. Gen trfr is sometimes back energised via the Aux trfrs. Would that be an issue?
I am concerned that the 23kV bus, two auxiliary trfrs and the gen trfrs are subjected to the voltage rise on the healthy phases longer than what is necessary. Danger is that fault could lead to another flashover which will be much more severe. Another concern is arcing faults with unearthed systems and the transient overvoltages.
Are my concerns valid or is 3s okay? Any other dangers? I was thinking of bringing it down to 0.1s.