Say you are doing a hand-calc for the fault contribution of a generator.
If an alternator is rated for 2000kVA, but the genset max output kW is 1500kW at a worst case PF of 0.8:
Which number do you use for short circuit fault contributions? The 2000kVA or the 1875kVA (1500/0.8)?
I would suspect that the fault contribution by the alternator is determined by the construction and winding impedances rather than the genset driving power.
I've asked two alternator manufacturers, and got conflicting answers: one said you can't contribute more than the genset driving power, and the other said genset driving power doesn't matter, its the inherent characteristics (impedances/reactaces/construction) of the alternator that determines the fault contribution.
So which one is it?
Thanks.
If an alternator is rated for 2000kVA, but the genset max output kW is 1500kW at a worst case PF of 0.8:
Which number do you use for short circuit fault contributions? The 2000kVA or the 1875kVA (1500/0.8)?
I would suspect that the fault contribution by the alternator is determined by the construction and winding impedances rather than the genset driving power.
I've asked two alternator manufacturers, and got conflicting answers: one said you can't contribute more than the genset driving power, and the other said genset driving power doesn't matter, its the inherent characteristics (impedances/reactaces/construction) of the alternator that determines the fault contribution.