Generator - fault current for downstream devices

Status
Not open for further replies.

mrbj

Electrical
Mar 2, 2004
32
Hi,
please help resolve the following discussion.
What value of rms sym fault current do you use when attempting to determine the settings of a downstream protective device (ie an mccb)when the supply is from a generator?.
Do you use either the sub-transient, the transient or the steady state conditions.
ie.
600kVA generator at 415/240Volt approx 835Amp
X"d at 0.10 giving Irms = 8350
X'd at 0.15 giving Irms = 5567
Steady state sus short circuit current at approx 2600A.
I err towards the transient, my collegue towards the steady state.

 
Replies continue below

Recommended for you

Subtransient for short circuit (electromagnetic) release and transient for overload / overcurrent release.
This works well in relay coordination studies.
 
Is this the same as the 1/2 cycle and 5 cycle numbers?
 
wbd:

I would say yes...may be rraghunath can pitch in again.
 
Normally three periods of concern, first the subtransient period, then the transient period, and finally a steady state period.
The subtransient period is short and has a time constant of 0.015 to 0.05 sec (0.9 - 3 cycles at 60hz, 0.75 - 2.5 seconds at 50hz)
The transient time constant have a typical range of 0.3 to 0.7 seconds (18 - 42 cycles at 60hz, 15 - 35 cycles at 50hz)

Short circuit calculations are often made for 3 different delay times, depending on the need. A first-cycle calculation is made for the withstand capability of equipment and fast interrupting times of fuses and low-voltage devices. In this case, the subtransient current is of concern. For high-voltage breakers that interrupt in 1.5 to 8 cycles, using an impedance that is a modified subtransient impedance would be reasonable. In fault calculations for time delay relaying of 0.3 to 0.5 seconds, use the transient current.

This is from A practical guide to short-circuit calculations by Conrad St. Pierre, a highly recommended book.
 