A coworker in our generation engineering department recently experienced this problem so I thought I’d check on here for some ideas for him, I’ll try to be brief, let me know if you need more information.
We had an 11.5kv, 9MW hydro unit out for 2 weeks of scheduled maintenance. During this yearly maintenance the plant operators also swap the leads to the field winding (why is this done?). They brought the unit up to speed and when the field was flashed the field ground relay (a GE PJG) tripped. When they were troubleshooting, they pulled the trip on this relay so that the field would flash, then put the trip back in and the unit got up to 4 MW before the relay tripped again. Throughout several tries the unit kept tripping at the transfer to exciter power and again at 4 MW of load.
The next day they were not even able to get load on the unit, the trip on the relay during the field flash was not intermittent like the day before, so they didn’t want to leave the test switch opened to try to bring it up to load. During troubleshooting they also put the leads to the field back to the way they were before the PM and the unit would not trip, it switched to exciter power and was brought up to load just fine.
Has anybody came across this problem, tripping the field ground relay only when the polarity is switched? Right now the unit is running just fine with the field polarity back to its pre-maintenance state.
We had an 11.5kv, 9MW hydro unit out for 2 weeks of scheduled maintenance. During this yearly maintenance the plant operators also swap the leads to the field winding (why is this done?). They brought the unit up to speed and when the field was flashed the field ground relay (a GE PJG) tripped. When they were troubleshooting, they pulled the trip on this relay so that the field would flash, then put the trip back in and the unit got up to 4 MW before the relay tripped again. Throughout several tries the unit kept tripping at the transfer to exciter power and again at 4 MW of load.
The next day they were not even able to get load on the unit, the trip on the relay during the field flash was not intermittent like the day before, so they didn’t want to leave the test switch opened to try to bring it up to load. During troubleshooting they also put the leads to the field back to the way they were before the PM and the unit would not trip, it switched to exciter power and was brought up to load just fine.
Has anybody came across this problem, tripping the field ground relay only when the polarity is switched? Right now the unit is running just fine with the field polarity back to its pre-maintenance state.