halms

Electrical
Mar 25, 2003
1
Has anybody ever heard of a Hydrogen cooled generator being damage due to a shorted field coil?
 
Replies continue below

Recommended for you

Are you suggesting that a shorted field coil isn't a problem with a hydrogen cooled generator?
 
Suggestion: The field protection relay may malfunction or be improperly set. Check with hydrogen generator manufacturers and service firms.
 
If you mean can a shorted field coil cause an explosion in a hydrogen cooled generator, NO! The air to H2 ratio is 99.9% H2, out of the explosive atmosphere range. If the H2 purity meter is operational this explosive atmosphere range would never be approached.
 
PS
The field protection relay is to detect field ground problems, not shorted turns.
Shorted turns occurr all the time. I have 5 turns shorted as we speak in one of my units. Repair is 16 months away and the unit has been operating for about 3 years this way.
 
To DougMSOE-You stated that the ratio of air to H2 is 99.9% H2. Should it not be the reverse ie H2 to air ratio?
 

chicopee — 0.1% hydrogen would not qualify the generator as hydrogen cooled.
 
chicopee, H2 cooled generators have almost total H2 in the generator. What small % of air is usually from the in-leakage around the bearings.
I guess I was not clear on this.
 
halms,
What was the extent of the damage? Was an explosion one of the manifestations?
 