Hi,
I am sure this topic must have been discussed many times here. I tried to search by using different key words but did not make it. You guys might be able to help.
The situation is, I came across a single line diagram where my job was to attach an emergency generator 2 MW,4160 V. Now, I looked at rest of the system and 4160/600 V system was high resistane grounded. I am not sure, what were the considerations. When I read these highly sophisticated discussions on this website about considerations while selecting type of grounding, It is just so exhaustive. Anyways, As per my understanding, these days, Low volatge systems are high resistance grouding systems to reduce arc flash energy. I am not sure, how they accomodate issues like when a ground fault happens in a small motor and the breaker does not trip because the system is high resistance grounded.
My question, what would should be the grounding type of this medium voltge generator feeding a transformer, a VFD and then a AC motor.
Here is what I know, Med. Voltage systems are low resistane grounded but I dont know why. low volatge systems are solidly grounded because it is made sure that there is enough ground fault current to trip low voltage breakers.
Could you please drop a word about this generator grounding.
I am sure this topic must have been discussed many times here. I tried to search by using different key words but did not make it. You guys might be able to help.
The situation is, I came across a single line diagram where my job was to attach an emergency generator 2 MW,4160 V. Now, I looked at rest of the system and 4160/600 V system was high resistane grounded. I am not sure, what were the considerations. When I read these highly sophisticated discussions on this website about considerations while selecting type of grounding, It is just so exhaustive. Anyways, As per my understanding, these days, Low volatge systems are high resistance grouding systems to reduce arc flash energy. I am not sure, how they accomodate issues like when a ground fault happens in a small motor and the breaker does not trip because the system is high resistance grounded.
My question, what would should be the grounding type of this medium voltge generator feeding a transformer, a VFD and then a AC motor.
Here is what I know, Med. Voltage systems are low resistane grounded but I dont know why. low volatge systems are solidly grounded because it is made sure that there is enough ground fault current to trip low voltage breakers.
Could you please drop a word about this generator grounding.