david h
Electrical
- Apr 28, 2020
- 2
I've done quite a few generator plants that tie into medium voltage utility networks. They ranged in size from 1.5MW to 5MW. The utility side in our area is 15kV grounded WYE. I've always specified the generators with a grounded WYE at either 5kV or 15kV but with a with a neutral grounding resistor. We use a transformer with a solidly grounded WYE for the utility connection and a DELTA on the generator side. This allows the neutral grounding resistor to work and gives the utility company the solid WYE that they require.
We've got a new project in the works and the utility company engineer is asking for a solidly grounded WYE-WYE transformer. If we hook it up with the generator neutral bonded to the transformer, we lose fault limiting of the neutral grounded resistor. Is there some other way to do this that I'm missing?
Many thanks
We've got a new project in the works and the utility company engineer is asking for a solidly grounded WYE-WYE transformer. If we hook it up with the generator neutral bonded to the transformer, we lose fault limiting of the neutral grounded resistor. Is there some other way to do this that I'm missing?
Many thanks