redtrumpet,
The fundimental difference on the type of genset system I am considering, is the potential for transverse generator movement when on isolators, either soft mounted to a genset skid or the skid isolators mounted to a concrete floor.
In either case, under start up, the set may roll quickly through different resonances. In addition, under fault conditions, say for instance full load rejection due to grid trip, then there will enevitably be some relative movement between the anchor point for the cable as it leaves the tray, or floor ducting, and the bushing box of a generator. This is the crux of the question and it is my belief that it is an overlooked but extremely essential consideration, when designing & installing the genset.
Hence my original question - albeit possibly too broad ranging, but then I need to start somewhere!
Experience tells me that where using steel wire armoured cable, it is good practice to include a cable sweep through a 90 Degree angle, something akin to 15- 20 times the diameter of that cable, with secure points of clamping at either end.
My recent review of some installations has shown what I believe is a horror of poor practice, where cables are being fully supported on bushings alone, with no cable clamping. I would like to understand where this practice comes from, & thought some esteemed engineers would be able to provide some direction to me.