An odd arrangement of five generators; 2-3500 kW gas turbines, 2-800 kVA gas engines and 1-800 kVA diesel unit, all rated at 11 kV and different rotational speeds. What is the best way to handle the neutral grounding of these different units?
1) Use a medium voltage switch or circuit breaker from the star point of each, then through the resistor and then to ground, or
2) Tie all star points together onto a common bus then to the resistor then to ground, with or without individual switches in each neutral lead, or
3) Connect the generator neutral to a fourth pole on the normal generator circuit breaker in the switchgear lineup, then to a neutral bus, then resistor, then ground, assuming one can find a MV circuit breaker manufactured with a fourth pole. This looks like an economical choice if the CB is available.
Any comments on safety or other ramifications of the different connections would be appreciated. Thanks to all.
1) Use a medium voltage switch or circuit breaker from the star point of each, then through the resistor and then to ground, or
2) Tie all star points together onto a common bus then to the resistor then to ground, with or without individual switches in each neutral lead, or
3) Connect the generator neutral to a fourth pole on the normal generator circuit breaker in the switchgear lineup, then to a neutral bus, then resistor, then ground, assuming one can find a MV circuit breaker manufactured with a fourth pole. This looks like an economical choice if the CB is available.