niallnz
Electrical
- Sep 16, 2001
- 99
I have recently installed a GE Multilin 489 generator protection relay onto a 4MVA 11kV 4pole synchronous generator, with brushless excitation. The star point of the generator is conected to earth via the primary of a 100:1 11/root3 transformer. The secondary of the transformer is connected directly to the Multilin Vneutral input (E10, F10).
When recommissioning the generator I noted that with the turbine running a speed and unsynchronised the measured neutral votage was approximately 300V. This was acceptable has the Multilin also displayed that they were some differences in the phase voltages. The generator was synchronised and loaded to 1MW with out adjusting the AVR. the neutral voltage dropped to 0V, as the system is strong and balanced. When the generator was manually tripped off, the measured neutral voltage when up to almost 3000V. Although the phase voltages were the same as before synchronisation. I turned off the AVR, and then turned it back on and the neutral voltage returned to its earlier value of 300V.
There have been occasions since, that when the AVR has been turned on the Multilin has tripped due to high neutral voltage (Fundamental). If the AVR is cycled the neutral voltage returns to normal.
As anyone got any ideas or tests that I can run. Thanks in advance.
When recommissioning the generator I noted that with the turbine running a speed and unsynchronised the measured neutral votage was approximately 300V. This was acceptable has the Multilin also displayed that they were some differences in the phase voltages. The generator was synchronised and loaded to 1MW with out adjusting the AVR. the neutral voltage dropped to 0V, as the system is strong and balanced. When the generator was manually tripped off, the measured neutral voltage when up to almost 3000V. Although the phase voltages were the same as before synchronisation. I turned off the AVR, and then turned it back on and the neutral voltage returned to its earlier value of 300V.
There have been occasions since, that when the AVR has been turned on the Multilin has tripped due to high neutral voltage (Fundamental). If the AVR is cycled the neutral voltage returns to normal.
As anyone got any ideas or tests that I can run. Thanks in advance.