nightfox1925
Electrical
- Apr 3, 2006
- 567
We have a 500kW, 600V Standby Diesel Generator at site with S.F. = 1.15, FLA = 601A, Max Overcurrent Rating = 1.8 x 601A for 60secs. P.F. = 0.80
The generator is protected by a 800AF molded case circuit breaker with Long time and Instantanous currents settings and associated time delays.
We have set the LTPU to be close to the FLA, hence LTPU = 0.75 (600A). The Instantaneous setting is disabled.
My question is, are we suppose to set the LTPU and time delays such that it will allow the 60 sec temporary overloading and trip instantly on the maximu fault. The present setting seems to trip the 1.8 x FLA at less than 1 second.
The generator is protected by a 800AF molded case circuit breaker with Long time and Instantanous currents settings and associated time delays.
We have set the LTPU to be close to the FLA, hence LTPU = 0.75 (600A). The Instantaneous setting is disabled.
My question is, are we suppose to set the LTPU and time delays such that it will allow the 60 sec temporary overloading and trip instantly on the maximu fault. The present setting seems to trip the 1.8 x FLA at less than 1 second.