hi All,
I want to have your opinions about PF, and reactive power:
1) why does generator with PF 0.85 lag to 0.9 lead have better flexibility in the Grid than PF 0.9 lag to 0.9 lead? is it because they can work in lower grid voltage?
2) our grid regulating body requires power plant to have 0.85 lag to 0.9 lead, does this mean they want to ensure that power plant can supply more VAR to support grid voltage drop? if yes, is it always voltage drops the power factor also drops (to lagging).
3) Who control grid power factor? is it regulating body or Is it grid frequency, power factor, voltage are related to the generating load vs consumers load?
4) If i have generator (H2 gas cooling) with rating of PF 0.85 lag, but in actual condition always works at 0.9 lag, from gen. capability curve does this mean the generator will require less H2 pressure at the same MW with 0.85 lag, while if at the same H2 pressure the generator can supply more MW?
5) why regulating body does not pay VAR but only MW? if grid voltage drops and regulating body requires a power plant to supply more VAR at the same load? so does this mean the generator excitation current will increase its current and affects steam turbine control valve to open wider? is this how to quantify the cost of VAR by more steam/fuel demand?
6) For 660 MW, which one is the best generator with PF 0.85 lag to 0.9 lead or 0.9 lag to 0.9 lead, what are the impacts to generator? is it 0.85 lag will require bigger size and why? what are other difference of 0.85 lag and 0.9 lag?
thanks for your answers
I want to have your opinions about PF, and reactive power:
1) why does generator with PF 0.85 lag to 0.9 lead have better flexibility in the Grid than PF 0.9 lag to 0.9 lead? is it because they can work in lower grid voltage?
2) our grid regulating body requires power plant to have 0.85 lag to 0.9 lead, does this mean they want to ensure that power plant can supply more VAR to support grid voltage drop? if yes, is it always voltage drops the power factor also drops (to lagging).
3) Who control grid power factor? is it regulating body or Is it grid frequency, power factor, voltage are related to the generating load vs consumers load?
4) If i have generator (H2 gas cooling) with rating of PF 0.85 lag, but in actual condition always works at 0.9 lag, from gen. capability curve does this mean the generator will require less H2 pressure at the same MW with 0.85 lag, while if at the same H2 pressure the generator can supply more MW?
5) why regulating body does not pay VAR but only MW? if grid voltage drops and regulating body requires a power plant to supply more VAR at the same load? so does this mean the generator excitation current will increase its current and affects steam turbine control valve to open wider? is this how to quantify the cost of VAR by more steam/fuel demand?
6) For 660 MW, which one is the best generator with PF 0.85 lag to 0.9 lead or 0.9 lag to 0.9 lead, what are the impacts to generator? is it 0.85 lag will require bigger size and why? what are other difference of 0.85 lag and 0.9 lag?
thanks for your answers