There is a case (bidding stage) of 140MW generator with 8500/5A ratio CTs and protective relays to be located about 200meters away.
This is an outdoor located gas turbine generator in a combined cycle gas power plant. The generator relay panels are located in electrical / control building that is about 200meters away.
I know the 5A CTs and the relays located in the same building (in case of steam based plants and gas based indoor plants).
Has any one come across a similar situation??
With a primary current of 8500A, is it a practical solution to go in for CTs with 1A secondaries (size issue). The CTs are located in isolated phase busducts (usual practice for this magnitude of currents).
Thanks in anticipation.