Generator reactance to use in harmonic load flow study 1

Status
Not open for further replies.

EddyWirbelstrom

Electrical
Feb 17, 2002
215
What synchronous generator reactance should be used in a harmonic study ?
Saturated sub-transient x"d, saturated transient x'd, saturated synchronous xd ?
 
Replies continue below

Recommended for you

For "load" of any sort, which implies a steady state condition, they only impedance to consider would be the synchronous. For a generator running near its rating it would be the saturated synchronous impedance and for one that's lightly loaded it would be the unsaturated. The transient and subtransient impedances are useful for fault and other non-steady state conditions.