I am working on an older Generac generator for a customer who is going to use this unit in a different application. The voltage is 208/120 parallel wye. I am going to change it to 240/120 double delta. The gen is a 1998 trailer unit and I have not found any resources on a reconfiguration for this gen end. The windings are not labeled NEMA standard. I have tried mec alte drawings because they were numbered the same as mine but I had to shut it down as soon as it excited because the engine loaded up. I've tried Generac's achieves but with no success. Any help in identifying my windings would really be a help. I have attached a data plate for the gen and a crude drawing of my original configuration. The 12 leads were numbered as they appear on the drawing. My model number is 98A03931-S. My serial number is 2042813. My windings are 1-2, 3-4, 5-6, 7-8, 9-10, 11-12. This is far from Generac's normal of 1-4, 2-5, 3-6, 7-10...... Any help would be appreciated.
 
Replies continue below

Recommended for you

Why not use Zig-Zag? (Edit)
One connection change and a continuity check.
No need for wire numbers.
This is a recognized three phase to single phase connection.

Label your wire pairs L1, L2, and L3.
Your numbers don't have to correspond to existing numbers.
If you picked L2, Use a continuity tester to find the corresponding neutral end of the L2 winding and label it L2n.
Connect L2n to L3 and insulate and forget it.
You will now have 120/240 Volts single phase between L1, N and L2.
You don't have to use L2.
If you identify any neutral end of a winding and connect it to either of the other two line leads and then insulate the connection, you will have 120/240 Volts single phase between the remaining two leads and neutral.
So much quicker, easier and safer than double delta.
This was once the standard single phase connection shown on older sets for single phase use.
 
Last edited:
Thanks for the connection instruction. My drawing and data plate was too much data to attach. So I wrote my winding numbers along with the model and serial at the bottom of the page. When you say double wye you are talking about what I call parallel wye. So starting with that I change a few connections and can produce 240 L-L
120 L1-N and 120 L2 to N. Is this right? I am drawing out your instructions right now.
 
In this their any disadvantage or loss to this configuration? Is it more or less efficient than a double delta? Is your recommended connection considered a zigzag configuration?
 
My original connection was:
L1- 7,5
L2-1,9
L3- 4,12
N- 3,8,6,10,2,11

Again though this looks off my windings are:
1,2
3,4
5,6
7,8
9,10
11,12
I chose L3 because of my wire routing. I took 3,11 and connected to 1,9 which was L2. I got 240 L-L. L1-N- 120. L2-N was 208. Was my choice of connection the problem. Should I have taken 3,11 to 7,5? This is my first restrap without an available diagram. I'm learning. I hope.
 
I mis-spoke.
I said "Double Wye" when I meant to say "Zig-Zag" connection.
So easy.
Just disconnect one phase neutral leads.
Do a continuity check and connect the leads to either of the other phase lines and tape up.
Connecting the neutral of one phase to either of the other two phase lines will give 120/240 Volt single phase, with no phase angle shift between the 120 Volt windings.

There is a related connection called the "Collin's connection" or Bar-Diamond connection, that will give the same result with ten lead generators. (Delco once made a lot of ten lead machines. They were commonly found in Telco take-outs. One wye point connection was buried with one lead only brought out.
Eg: leads 10, 11, and 12 were connected internally and only lead 10 was brought out.

The zig-zag has been ued by major gen-set manufacturers.
Voltage drops and losses are the same.
Both double delta and zig-zag reduce the KVA capacity by 1/3.
The kW capacity is dependant on the prime mover and will increase to the KVA capacity.
EG: PF 0.8 or 80% becomes PF 1.0 or 100%.
Actually, The set will be overpowered and available input kW will be 120% of allowable KVA.
(power factor of 1.2, but not to imply over-unity??)
 
Forget the numbers.
Just disconnect one set of neutral leads, check continuity and reconnect to a different phase line.
You will have used one of six possible connections.
It just doesn't matter.
All six possible connections give the same 120/240 Volts.
 