Mohsin Jameel
Electrical
- Apr 22, 2021
- 2
Generator of 400 V 1250 KVA shows Max 3 Phase Short circuit current of 19 KA . In my opinion it is the maximum three phase SKA that Generator can produce obviously can produce higher P-G fault being solid ground.
We have 3 Generators in parallel.
My question and confusion is that when we model it in ETAP software its 3 phase fault contribution on ETAP run when considering fault at Main bus comes out to be more than 19 KA. Is it possible that generator with rated/datasheet mentioned capacity of 19 kA can feed 24-26 kA in any case.
Should we need to tune ETAP modelling to restrict fault current to 19 kA or is it possible that generator can feed fault current more than fault current mentioned on its datasheet
We have 3 Generators in parallel.
My question and confusion is that when we model it in ETAP software its 3 phase fault contribution on ETAP run when considering fault at Main bus comes out to be more than 19 KA. Is it possible that generator with rated/datasheet mentioned capacity of 19 kA can feed 24-26 kA in any case.
Should we need to tune ETAP modelling to restrict fault current to 19 kA or is it possible that generator can feed fault current more than fault current mentioned on its datasheet