with a standby application, is it typical to use a temp. rise of 105 deg. C or 130 deg. C? We are concerened with the heating affects of harmonics and are considering specifying a low temperature rise for the alternator.
 
Replies continue below

Recommended for you

Specifying a rise doesn't buy you much unless you also specify the insulation class.

Some people in attempt to gain thermal margin will specify that the machine be limited to a rise one insulation class below the actual insulation class of the machine.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Typical spec would be to insulate the machine for temperature Class F, but to operate with a Class B rise. This ensures that you have plenty overload margin and the insulation should have a much extended life.


----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!
 
For small gensets <2MW, it's common to insulate at class H (180C) and specify 105C rise. With the standard 40C ambient, this gives you a good margin of 180 - (105 + 40) = 35C. Some engineers specify large margins in hopes of obtaining better life or to better withstand the increased heating effects when high harmonic loads are being supplied.
 