mgtrp
Electrical
- May 4, 2008
- 326
I have a somewhat unusual case of having several 2MVA generators that although star-connected, cannot have the neutral point earthed due to their unconventional construction.
The generators will feed into a common step-up transformer, with no loads (other than static excitation) fed directly. Another conventionally connected and earthed generator will feed into a tertiary winding on the step-up transformer. The step-up transformer then has some plant loads supplied from it, and feeds into a star-star utility transformer with delta tertiary.
The options that I am aware of for earthing the generator system are either to provide a dedicated earthing transformer (zig-zag or star-broken delta), or to use a step-up transformer with a star-connected LV winding. Either way, the earthing will be a HRG system.
If a earthing transformer is used, I see the arrangement as being to use delta-connected windings for the generator side of the step-up transformer and star-connected windings for the utility side and don’t believe that there are any great technical problems to solve.
However, it has been suggested that the equipment requirements could be simplified using a star-connected step-up transformer winding to earth the generators. A delta winding would still need to be provided, and this could be achieved in the tertiary winding (with the conventional generator connected), or on the high-voltage winding.
A delta winding would be needed somewhere, either the tertiary winding or the HV winding, and in either case I’m not sure where it would be better located (probably the HV winding?), or even if two delta windings should be used (probably not?).
Any suggestions, or advice of possible hooks to look out for would be much appreciated on the above (slightly long-winded, I apologize) story.
The generators will feed into a common step-up transformer, with no loads (other than static excitation) fed directly. Another conventionally connected and earthed generator will feed into a tertiary winding on the step-up transformer. The step-up transformer then has some plant loads supplied from it, and feeds into a star-star utility transformer with delta tertiary.
The options that I am aware of for earthing the generator system are either to provide a dedicated earthing transformer (zig-zag or star-broken delta), or to use a step-up transformer with a star-connected LV winding. Either way, the earthing will be a HRG system.
If a earthing transformer is used, I see the arrangement as being to use delta-connected windings for the generator side of the step-up transformer and star-connected windings for the utility side and don’t believe that there are any great technical problems to solve.
However, it has been suggested that the equipment requirements could be simplified using a star-connected step-up transformer winding to earth the generators. A delta winding would still need to be provided, and this could be achieved in the tertiary winding (with the conventional generator connected), or on the high-voltage winding.
A delta winding would be needed somewhere, either the tertiary winding or the HV winding, and in either case I’m not sure where it would be better located (probably the HV winding?), or even if two delta windings should be used (probably not?).
Any suggestions, or advice of possible hooks to look out for would be much appreciated on the above (slightly long-winded, I apologize) story.