One of our 130MW generators tripped on mechanical lockout relay due to very high vibration of Lower Guide Bearing. The trip is set at 15mils. Normally the vibration was found around 1 to 2 mils. We inspected for any looseness of fasteners, locking system of rotor and stator. Also checked the runner buckets, jets and associated system, inspected for any lost weights inside the rotor portion which were originally present in the rotor at the time of commissioning itself, but nothing found. Then we checked the impedance of all rotor poles. We found that the values were similar for all poles. The appearance of poles were similar, i.e., no shearing and shifting. The interpolar spaces were also checked for any looseness, but nothing found.
After these checks the generator was test started for vibration measurement using another test kit at different loads. Found that the Lower Guide Bearing vibration level gradually increasing while loading and observed 200micro meter at 100MW. Observed 8mils vibration in the panel meter at that time and found increasing while loading further. So we stopped the generator, filtered the bearing oil and analyzed the filtrate sample for checking the presence of any metal particles, nothing observed seriously.
I request your valuable remarks about where should be the fault, which caused vibration. I also request you to give advices for how to proceed further for further checks and for remedial actions.
With regards,
appunni
One of our 130MW generators tripped on mechanical lockout relay due to very high vibration of Lower Guide Bearing. The trip is set at 15mils. Normally the vibration was found around 1 to 2 mils. We inspected for any looseness of fasteners, locking system of rotor and stator. Also checked the runner buckets, jets and associated system, inspected for any lost weights inside the rotor portion which were originally present in the rotor at the time of commissioning itself, but nothing found. Then we checked the impedance of all rotor poles. We found that the values were similar for all poles. The appearance of poles were similar, i.e., no shearing and shifting. The interpolar spaces were also checked for any looseness, but nothing found.
After these checks the generator was test started for vibration measurement using another test kit at different loads. Found that the Lower Guide Bearing vibration level gradually increasing while loading and observed 200micro meter at 100MW. Observed 8mils vibration in the panel meter at that time and found increasing while loading further. So we stopped the generator, filtered the bearing oil and analyzed the filtrate sample for checking the presence of any metal particles, nothing observed seriously.
I request your valuable remarks about where should be the fault, which caused vibration. I also request you to give advices for how to proceed further for further checks and for remedial actions.