Hi all i posted this in the power engineering section and got some great responses. just posting here in case anyone might have anything else to offer many thanks Flashover
Flashover (Electrical) Feb 3, 2005
Hi All,
interesting one for the board.
we have 150 Mwatt, 181.2 MVA generator (onto 110kV system), when operated at unity power pactor or slightly lagging we have no problems. however when run at full load and 0.85pf lagging we get vibration levels rising rapidily after about three hours (i.e there seems to be a thermal lag effect, everything reasonably steady then vibrations just take off)
having examined the vibrations on Bently Nevada scope we see that the vibration is 1 * Frequency, i.e 50Hz vibration which leads me to the conclusion of shaft imbalance brought on by shaft bending or rotor coils shifting.
has anybody experienced similar problem??
would love to hear views on the above.
Many thanks
Flashover
Flashover
Eng-Tips Forums is Member Supported. Click Here to donate.
byrdj (Mechanical) Feb 3, 2005
Does the vibration levels go down when load is reduced?
Many years ago, (~1970 vintage units same size as yours). units had similar increase in vibration brought on by exceeding a field current level (load and pf dependant). once vibration got rough, to reduce the vibration, the unit had to be taking off line and speed drooped to less than 500 rpms (back to gear for an hour was the practice). the problem was with the support for the end turns under the retaining ring. as the field bar expanded with current, the suport would stick and cause an endturn to buckle. The fix was replacing the end turn insulation (removing the retaining rings).
You may want to ask a repair facility if this could be a common problem for your design.
Hope your problem is not as costly.
Good luck
Flashover (Electrical) Feb 3, 2005
The vibrations go back to normal operating levels when the power factor is restored to Unity. we can then continue to operate at full load.
we are now testing at 0.95, 0.90 etc
cheers
Flashover
byrdj (Mechanical) Feb 3, 2005
are you operating within design. I pulled a capibility curve I had. it showed MWs needed to be reduce to 90% when going from 90 to 85 Pf.
This would be an operating range where field heating is great. I don't have a answer, but suggest looking at the field cooling. If H2 cooled, besure the coolers are vented and flows set to balance delta T. changing the cooler exit temp may help. Purity and pressure should be verified also
Flashover (Electrical) Feb 3, 2005
Hi all,
its an air cooled machine.
the gaurantee is 150 MW at 0.85pf.
any suggestions for further investigations that may help?
thanks
Flashover