We are currently assessing the condition of a three-phase 2.5 kVA, 400V emergency generator, which is used for black start only. During our routine checks, we observed the following insulation resistance values:
• Initial readings (before cleaning):
• Phase to ground (IR): as low as 404 kΩ
• Phase to phase: approximately 1.2 MΩ
We then dismantled the rotor and performed the following maintenance steps:
• Cleaned the windings with isopropyl alcohol
• Coated the sleeve with electrical varnish
• Dried the unit using an air dryer
Post-maintenance insulation readings:
• Phase to ground: improved significantly to 1 GΩ
• Phase to phase: now reads 15 MΩ
My question is:
Are these 15 MΩ phase-to-phase readings acceptable for such a small generator used only for emergency/black start purposes? Or should further action be considered to improve these values