generetor capacity

Status
Not open for further replies.

immi2663

New member
Nov 6, 2014
2
i have a 3 phase 50hz generator.its load capcity given by OEM is 60kVA.this 60Kva is the total capcity of all 3 phases or 60kva per phase. This generator can handle 60kVA by all 3 phases or 3 phases can handle 60,60 and 60 Kva each means 180 kVa total.
 
Replies continue below

Recommended for you

60kVA total, balanced evenly across the three phases and generally not exceeding 20kVA on any phase.
 
It is 60kVA total. You need to consider the kW output from your prime mover as well.