Suggestions:
1. Low voltage power distribution system having the supply with star connection usually has its neutral solidly grounded. This is because of advantages of solidly grounded neutral in terms of simplicity, applicability to dual voltage systems e.g. 208/120, and relatively small damage be the short circuit arc (relatively small short circuit arc energy is released).
2. Medium voltage (1kV-100kV), especially on its lower end, has frequently applied a resistor, which is often called "medium resistance system neutral grounding." However, there is some applicability advantages and disadvantages to be considered. Therefore, there is another type frequently used, which is called the "high-resistance system neutral grounding." This type of grounding allows much smaller current to produce arcing at the fault and it can be traced where the arc is. The fault can be cleared within a short time or stay the longer time depending on the insulation level (100%, 133%, etc.). D. Beeman "Industrial Power Systems Handbook", McGraw-Hill, 1955 describes this methods fairly popularly.
3. If there are more power supplies with the star connection, then one high or medium resistance grounding is implemented at one power supply since it is sufficient and convenient. In case that maintenance and testing are to be done on the power supply that has the neutral grounding in effect, then the grounding system is switched to another power supply so that the high or medium resistance grounding has the continuous functionality of the power distribution system.