X49
Electrical
- Apr 30, 2009
- 106
We upgraded a water pump to 50hp and added a solid state soft starter. We have an existing 60kW Cummins gas genset that will start up the pump most of the time, but often surges once the pump is almost up to speed, struggling to keep a constant speed. Sometimes the generator trips on overspeed.
The generator is has a PMG alternator and 3-phase rectifying regulator. We have tried playing with the soft start settings (Current ramp w/ different current limits, power ramp, etc.) but without success.
I suspect that replacing the genset with a larger one will fix this issue but I am open to suggestions for an easier fix.
The generator is has a PMG alternator and 3-phase rectifying regulator. We have tried playing with the soft start settings (Current ramp w/ different current limits, power ramp, etc.) but without success.
I suspect that replacing the genset with a larger one will fix this issue but I am open to suggestions for an easier fix.