I was involved with a short experiment that illustrated this point.
Case; A small power plant, 2 x 600 kw gensets,plus 3 x 350 kw gensets.
The load is slightly over 600 kw and two generators are running. This is a common occurance.
The 600 kw set was rated 0.8 PF and was running close to 0.8 PF.
We think that if we correct the power factor with capacitors, we can run up to 750 kw and avoid the need for the second set.
We feel that we can safely overload the 600 kw set for a few minutes to test our theory. By adjusting the governors we start to overload the 600 kw set. At about 608 kw, the engine starts to lose speed and the frequency starts dropping.
Conclusions;
The maximum kw is determined by the power of the engine.
The engine in question was capable of producing 600 kw and no more.
A second illustration is the application of single phase generators in size ranges above about 20 kw.
At least one major gen-set manufacturer does not use single phase alternators above about 20 kw., nor do they assemble single phase sets above that size. They supply the single phase market by reconnecting and rerating three phase sets.
For example, a set may be rated at 50 KVA, 40 KW, 0.8 PF, three phase. If a single phase set is required this set may be reconnected in either zig-zag, or double delta.
The new kva rating is 2/3 of the original rating, or 33 KVA.
The same engine is used so there is enough power for 40 KW.
The new rating will be, 33 KVA, 33 KW, 1.0 PF.