CBGUY
Electrical
- Nov 1, 2013
- 3
Device BE3-47N. tripping when set for 10%, never trips when set for 15% DRANETZ reports 1% or less. Waveform has flat spot at at zero crossing. Two devices do exact same thing. I think Specifying engineer has too tight a value. Any ideas. Load is a data center and building mechanical. Happens on primary and alternate generator. New CATS.