I have a 480 volt switchboard with a 1600 amp main circuit breaker with a GE type SS circuit breaker with ground fault trip, and feeder breakers of GE type SGH, SGL, SFH downstream of the main. These breakers feed lighting panels and rooftop units.
Some of the feeder breakers and the main are experiencing nuisance trips (I think I was told that it was at least some of the rooftop feeders). The nuisance trips have subsided since the GE rep came out and cranked the trip settings up, I think.
I figured the best way to troubleshoot is to turn on all the rooftops and lights/loads I can find, and read the current in the main switchboard from neutral to ground. If there is more than "leakage" type current reading there, I could then 1) shut down hvac units 2)shut down lights/loads 3)trip breakers if necessary to identify which circuits have an effect on the amount of neutral-ground current. Once the offending circuits are found, they can be traced down to figure out where the problem is, fix it and reset the GF sensors to some level that might kind of coordinate (I didn't include a zone-selective scheme on the GF - mea culpa).
I am assuming the contractor somehow made a downstream connection between neutral and ground - otherwise we would have had an equipment burndown by now.
Any thoughts?
Some of the feeder breakers and the main are experiencing nuisance trips (I think I was told that it was at least some of the rooftop feeders). The nuisance trips have subsided since the GE rep came out and cranked the trip settings up, I think.
I figured the best way to troubleshoot is to turn on all the rooftops and lights/loads I can find, and read the current in the main switchboard from neutral to ground. If there is more than "leakage" type current reading there, I could then 1) shut down hvac units 2)shut down lights/loads 3)trip breakers if necessary to identify which circuits have an effect on the amount of neutral-ground current. Once the offending circuits are found, they can be traced down to figure out where the problem is, fix it and reset the GF sensors to some level that might kind of coordinate (I didn't include a zone-selective scheme on the GF - mea culpa).
I am assuming the contractor somehow made a downstream connection between neutral and ground - otherwise we would have had an equipment burndown by now.
Any thoughts?