GFCI at a lower voltage.

Status
Not open for further replies.

jpl5085

Electrical
Jan 16, 2001
6
Can a GFCI 120V Class A (5mA) be used at 24VAC? I am using as a pass-through device for downstream protection in a control panel.
 
Replies continue below

Recommended for you

There’s a novel Leviton GFCI that may do the job. See: It needs external 120V power but the protected circuit wiring (24V in your application) passes through a molded-in current transformer. It has to be used with an external contactor to disconnect the protected circuit for a ground fault, though.
 