I have a question about installing a GFCI on a machine which has a number of components, some of which run on 208V 3-phase and others on 120V single-phase. Is it possible/safe to install a GFCI at a single 208V 3-phase input to the machine and split the 120V loads off after the input using a single hot wire and the neutral? Would a GFCI made for 208V three-phase work? Thanks, in advance.
 
Replies continue below

Recommended for you

I am not familiar with 208 GFCI. Does the model you have in mind sum all 3 phases as well as neutral? If yes, then single phase loads should not bother it. As long as Ia+Ib+Ic+In are 0, then all is well. If it istead assumes a delta load, and really only sums Ia+Ib+Ic, and ignores In, and you connect a load that will cause In > 0, you are going to trip.
 
That's the conclusion that I had arrived at, but I wanted to check with others to see what they think. However, another part of my problem is where to find such a device. I had found a GFCI that claimed to work for 208-240V 3-phase, but it has very limited documentation and is a bit of a black box. As far as I can tell, it seems like it is assuming a delta load (and input for that mattter), as it functions correctly for a three-phase load, but trips when any 120V single phase load is connected.
Anyone know of a GFCI that would work in this situation?
 
We need to have more experienced people chime in on this one. But for my 2 cents worth, I have seen people put zero sequence CTs on three phases + neutral and run the output to rather some inexpensive relay (Crompton or such) and then to a breaker shunt trip, but I do not think they were highly sensitive. Mostly at 208V you get breakers with ground fault functions built in, but again I do not think they are commonly as sensitive as GFCI.
 
I don't think you're going to find what you are looking for. What is the purpose of the ground fault protection - for operator safety or equipment protection?

If you are just trying to detect ground faults, a molded case breaker with a solid-state trip unit including ground fault would do what you want, but you would need a neutral sensor in addition to phase sensor.

If you are trying to match the function of a standard single-phase GFCI breaker or receptacle, that is another matter. These operate at a much lower current level to prevent electrocution. Best bet for this would be to add GFCI receptacles or breakers for your single-phase loads downstream of the three-phase breaker.
 
There are two options that I know of.

#1 - Startco SE-502 relay (startco.ca). This relay basically resistance grounds the neutral of a Y supply transformer and trips a under-voltage coil in a breaker. I have used one of these and tested it works with 6mA of ground current.

#2 - Bender LifeGuard GFCI (bender.org). This is a complete relay/breaker/transformer UL listed unit that provides the ground fault protection.

 
check out square d's web site....they offer three phase ground fault relays for great for motor applications...we had to hook up a bunch of mitsubishi ductless split a/c units.....big warning on their literature to provide "ground leakage detection"...sounded like gfci to me....relays have under voltage detection too....
 
The Eaton (Cutler-Hammer) family of "Earth Leakage" breakers would be a consideration. These will often be the easiest to implement compared to the external ground fault modules such as Square D. Also, they probably have a better range of settings.
 
30mA three pole or 3-pole + neutral RCDs are fairly common in the UK. They use the same principle as the single pole RCDs - a core balance CT with a sensitive tripping circuit. I don't recall seeing them with a 10mA rating because under UK legislation that is only required in higher risk environments. The standard RCD (Residual Current Device - GFCI to North Americans) for personnel protection is a 30mA setting.

Here's Schneider's offering:



----------------------------------
image.php

Sometimes I wake up Grumpy.
Other times I just let her sleep!
 
We had some 3 phase applications of for the mits a/c outdoor a/c units....ocp required like 60A/3p could not find any commercially available cb's(us) with gfci....went with the relay....
 