I'm currently reviewing a submittal that indicates residual-type ground fault detection to be provided for an existing ungrounded 12,470-volt system that currently has no ground fault indication. I'm rejecting this because I do not believe this can work.
My first preference would be detection of zero-sequence voltage. Unfortunately, it is probably not possible to install PT's anywhere on this system due to space restraints.
Therefore, I'm considering zero-sequence current detection. I'm still not convinced this will work, but have not been able to find any real documentation either way.
Any thoughts?
My first preference would be detection of zero-sequence voltage. Unfortunately, it is probably not possible to install PT's anywhere on this system due to space restraints.
Therefore, I'm considering zero-sequence current detection. I'm still not convinced this will work, but have not been able to find any real documentation either way.
Any thoughts?