What is the difference between GLBS(generator load break switch) and GCB(generator circuit breaker)applied to power plant porject.
I got caught with contractor that they proposed GLBS to be used for 1000MW coal fired power plant instead of GCB. The plant is connected to 500kV switchyard and has no start up transformer from power grid but back energizing from grid through generator step-up transformer and Unit Auxiliary Transformer while, at the time of back start, the GLBS is opened. They explained that if fault happens at generator system voltage, they will trip 500kV CB, 11kV CBs at the incomer of 11kV switchgear and trip 41E field CB.
Is there any problem if this is to be GLBS instead of GCB. How about if the fault happens at Unit Aux Transformer, even though field CB is tripped, the fault current still feeds from generator to the UAT. This increases damages to UAT ?
If the GCB is not necessary, why does the combined cycle power plant still need to use GCB instead of GLBS in every projects ? why don't they use GLBS which is cheaper ?
I got caught with contractor that they proposed GLBS to be used for 1000MW coal fired power plant instead of GCB. The plant is connected to 500kV switchyard and has no start up transformer from power grid but back energizing from grid through generator step-up transformer and Unit Auxiliary Transformer while, at the time of back start, the GLBS is opened. They explained that if fault happens at generator system voltage, they will trip 500kV CB, 11kV CBs at the incomer of 11kV switchgear and trip 41E field CB.
Is there any problem if this is to be GLBS instead of GCB. How about if the fault happens at Unit Aux Transformer, even though field CB is tripped, the fault current still feeds from generator to the UAT. This increases damages to UAT ?
If the GCB is not necessary, why does the combined cycle power plant still need to use GCB instead of GLBS in every projects ? why don't they use GLBS which is cheaper ?