Hello
I am doing a desktop study looking at grading between HRC fuses and downstream MCBs. The upstream fuses tend to be GEC Alstom type 'T' HRC to BS88 and I have obtained data including the 'pre-arcing' values.
For the downstream MCBs, I need to make sure that at the particular DB fault level, the let through energy of MCB is lower than the pre-arcing of the fuse so that the MCB goes first as intended.
The problem I have is that the downstream MCBs are GEC Vynckier and I have not been able to obtain any information on these (even from GE direct).
Q1 - Can anyone point me towards any information on GEC Vynckier or similar Type 2 MCBs so that I can make this assessment?
I have done some calcs with Memshield data and this is showing a very high number of locations where there is no grading; eg with a 63A fuse upstream and a 32A MCB downstream there is only grading to 1.5 kA FL. On my site there are a lot of DBs with fault levels up around 7 – 10 kA (three phase – though most of the MCBs though are single phase).
Q2 - Does 63A immediately jump out as being far too small a fuse for a 32A downstream MCB?
Q3 - any other info on the issue of grading fuses with MCBs would be appreciated.
Thanks in advance
Simon
I am doing a desktop study looking at grading between HRC fuses and downstream MCBs. The upstream fuses tend to be GEC Alstom type 'T' HRC to BS88 and I have obtained data including the 'pre-arcing' values.
For the downstream MCBs, I need to make sure that at the particular DB fault level, the let through energy of MCB is lower than the pre-arcing of the fuse so that the MCB goes first as intended.
The problem I have is that the downstream MCBs are GEC Vynckier and I have not been able to obtain any information on these (even from GE direct).
Q1 - Can anyone point me towards any information on GEC Vynckier or similar Type 2 MCBs so that I can make this assessment?
I have done some calcs with Memshield data and this is showing a very high number of locations where there is no grading; eg with a 63A fuse upstream and a 32A MCB downstream there is only grading to 1.5 kA FL. On my site there are a lot of DBs with fault levels up around 7 – 10 kA (three phase – though most of the MCBs though are single phase).
Q2 - Does 63A immediately jump out as being far too small a fuse for a 32A downstream MCB?
Q3 - any other info on the issue of grading fuses with MCBs would be appreciated.
Thanks in advance
Simon