ivanngwh
Electrical
- Jan 1, 2007
- 7
I have to connect a LV renewable generator to the utility's LV grid.
The LV renewable generator is 380V, TPN, 50Hz, 1500kVA, 12.3MVA fault level contribution.
The utility transformer LV side is 380V, TPN, 50Hz, 2000kVA, 24MVA fault level.
When coupled, the total fault level is about 12.3+24=36.3MVA thus the fault current is about 55kA.
The utility company said that his transformer LV terminal will damage when the fault current is >40kA and therefore the grid connection scheme is rejected.
Somebody said that the simplest solution to the present problem is to add a high breaking capacity fuse (say 2500A 40kA) on the LV renewable generator side so that its fault current will not flow to the utility transformer's LV terminal.
Then, the utility transformer LV terminal will never experience a fault current of >40kA in all situations.
Is this simple scheme feasible?
If yes, what kind of fuse is suitable for this application?
I have no experience in buying fuse of such large rating or even special characteristic fuse (if required).
Thanks
Ivan Ng
The LV renewable generator is 380V, TPN, 50Hz, 1500kVA, 12.3MVA fault level contribution.
The utility transformer LV side is 380V, TPN, 50Hz, 2000kVA, 24MVA fault level.
When coupled, the total fault level is about 12.3+24=36.3MVA thus the fault current is about 55kA.
The utility company said that his transformer LV terminal will damage when the fault current is >40kA and therefore the grid connection scheme is rejected.
Somebody said that the simplest solution to the present problem is to add a high breaking capacity fuse (say 2500A 40kA) on the LV renewable generator side so that its fault current will not flow to the utility transformer's LV terminal.
Then, the utility transformer LV terminal will never experience a fault current of >40kA in all situations.
Is this simple scheme feasible?
If yes, what kind of fuse is suitable for this application?
I have no experience in buying fuse of such large rating or even special characteristic fuse (if required).
Thanks
Ivan Ng