Kiribanda
Electrical
- May 6, 2003
- 697
Hello all members,
The following issues are regarding a Ground grid design for a 230 kV outdoor switchyard.
Assume the switchyard feeding an industrial plant consists of a step down transformer of 230 to 13.8 kV. The network has got the following allowable or calculated P-E fault currents.
230 kV side - 10 kA (Feeding from the Utility)
13.8 kV level – 400 A (Low resistance grounding)
480 V LV level – 20 kA (Solid Grounding)
1)If a Ground grid is to be designed for the 230 kV outdoor switchyard, what should be the value of the grid current out of above three, to be taken for calculating the step, touch, GPR voltages etc.?
2)If the maximum earth fault current value on the network is taken as the Grid current regardless of the voltage level, in this example 20 kA, then is it an over designed, expensive ground grid?
3)Is it necessary to design a ground grid by taking the grid current as 20 kA for LV substations even though it is an indoor substation?
4)Are ground grids installed under the concrete floors of an indoor substation too?
Your valuable inputs are welcome!
Regards!
Kiribanda
The following issues are regarding a Ground grid design for a 230 kV outdoor switchyard.
Assume the switchyard feeding an industrial plant consists of a step down transformer of 230 to 13.8 kV. The network has got the following allowable or calculated P-E fault currents.
230 kV side - 10 kA (Feeding from the Utility)
13.8 kV level – 400 A (Low resistance grounding)
480 V LV level – 20 kA (Solid Grounding)
1)If a Ground grid is to be designed for the 230 kV outdoor switchyard, what should be the value of the grid current out of above three, to be taken for calculating the step, touch, GPR voltages etc.?
2)If the maximum earth fault current value on the network is taken as the Grid current regardless of the voltage level, in this example 20 kA, then is it an over designed, expensive ground grid?
3)Is it necessary to design a ground grid by taking the grid current as 20 kA for LV substations even though it is an indoor substation?
4)Are ground grids installed under the concrete floors of an indoor substation too?
Your valuable inputs are welcome!
Regards!
Kiribanda