alexcao
Electrical
- Feb 10, 2011
- 3
Hello - at our power plant, we have motor starters that use a CBCT (core balance current transformer) to measure zero sequence current on the motor phases. It's one of those window-type CTs with all three phase of the AC motor passing through the center. The CT ratio is 50:0.025 and it has a ge multilin relay connected to it. I am a bit clueless as to how to set the primary current pickup level as the relay setting can range from 0.5 to 15 A. I've looked through the Blackburn book for protective relaying and in the IEEE 242 buff book and both call out a primary sensitivity of 5-10 A, but nothing I've found has given me a good grasp of how to really calculate or determine a good threshold for ground current. Should the ground current really be that high? I thought its typically in the sub-amp level?
Was wondering if anyone could help me with the following questions I have?
1. Does the ground current pickup for a sensitive ground CT (in this case CBCT) depend on the motor size?
2. How do you calculate or determine accurately a good ground current pickup level for a motor with a 50:0.025 CT to prevent from nuisance tripping but still adequately protecting the motor from a ground fault?
Any help is appreciated
Was wondering if anyone could help me with the following questions I have?
1. Does the ground current pickup for a sensitive ground CT (in this case CBCT) depend on the motor size?
2. How do you calculate or determine accurately a good ground current pickup level for a motor with a 50:0.025 CT to prevent from nuisance tripping but still adequately protecting the motor from a ground fault?
Any help is appreciated