CoolB00Yz
Electrical
- Nov 14, 2007
- 5
Hey Guys.
We are commissioning 2 4000HP motors via 4KV controlgear. The issue we are facing is that both motors keep tripping during commissioning performing motor solo run. They are both tripping on 50N Ground Fault via SEL-710 relay. Ground fault current detected via CBCT 50:5. The setting was originally 10 Amps at 50ms and changed to 10 Amps at 100ms but still tripped. FYI, both motors FAT was done successfully. Power cables and motors were meggered, and winding balance.
What can we do further to proceed and perform motor solo run? It has been tiring 5 days.
Appreciate your input.
We are commissioning 2 4000HP motors via 4KV controlgear. The issue we are facing is that both motors keep tripping during commissioning performing motor solo run. They are both tripping on 50N Ground Fault via SEL-710 relay. Ground fault current detected via CBCT 50:5. The setting was originally 10 Amps at 50ms and changed to 10 Amps at 100ms but still tripped. FYI, both motors FAT was done successfully. Power cables and motors were meggered, and winding balance.
What can we do further to proceed and perform motor solo run? It has been tiring 5 days.
Appreciate your input.