I am trying to better understand how a ground fault in the 120 volt control portion of a 480 volt, 3 phase motor starter circuit can cause a ground fault alarm in our high resistance ground fault detection relay on our MCC.
We incurred a ground fault alarm on our 480 volt, 3 phase MCC. I looked at the ground fault relay, and it was showing 270 volts at about 3.3 amps. Our electrician determined that the start-stop station of was full of water, and was causing the ground fault. This is a size 5 starter, and the start-stop controls are 120 VAC via a 480/120 .100 KVA CPT (one side grounded) in the starter. The control is a basic 3-wire field start-stop station, operating a 120 volt control relay in the motor starter bucket, which in turn operates the 480 volt coil on the size 5 starter.
I know it happened, because when we cleaned the water out of the start-stop station, the ground fault went away. But I don't see how the ground fault went through (or around) the control relay and caused the high current (3.3 amps @ 270 volts) in the ground fault relay, without blowing the primary or secondary control fuses around the CPT.
We incurred a ground fault alarm on our 480 volt, 3 phase MCC. I looked at the ground fault relay, and it was showing 270 volts at about 3.3 amps. Our electrician determined that the start-stop station of was full of water, and was causing the ground fault. This is a size 5 starter, and the start-stop controls are 120 VAC via a 480/120 .100 KVA CPT (one side grounded) in the starter. The control is a basic 3-wire field start-stop station, operating a 120 volt control relay in the motor starter bucket, which in turn operates the 480 volt coil on the size 5 starter.
I know it happened, because when we cleaned the water out of the start-stop station, the ground fault went away. But I don't see how the ground fault went through (or around) the control relay and caused the high current (3.3 amps @ 270 volts) in the ground fault relay, without blowing the primary or secondary control fuses around the CPT.