In most areas of the USA, the NFPA 70 (NEC) is code.
Section 215.10 requires ground fault protection for feeders that are "1000 amperes or more and installed on solidly grounded wye electrical systems of more than 150 volts to ground, but not exceeding 600 volts phase-to-phase" unless "ground-fault protection of equipment is provided on the supply side of the feeder" etc.
The following examples are not services, but feeders:
If there was GFP on the primary of a delta-wye solidly grounded transformer (1000kVA, 480/277V secondary, separately derived source), would you consider the feeder on the secondary side of the transformer GF protected on it's supply side?
Is your answer the same if the input feeder to a 1000kVA dual conversion type UPS module, 480/277V output, separately derived source, is protected upstream by GFP? Is the output feeder of the module GF protected on it's supply side?
Section 215.10 requires ground fault protection for feeders that are "1000 amperes or more and installed on solidly grounded wye electrical systems of more than 150 volts to ground, but not exceeding 600 volts phase-to-phase" unless "ground-fault protection of equipment is provided on the supply side of the feeder" etc.
The following examples are not services, but feeders:
If there was GFP on the primary of a delta-wye solidly grounded transformer (1000kVA, 480/277V secondary, separately derived source), would you consider the feeder on the secondary side of the transformer GF protected on it's supply side?
Is your answer the same if the input feeder to a 1000kVA dual conversion type UPS module, 480/277V output, separately derived source, is protected upstream by GFP? Is the output feeder of the module GF protected on it's supply side?