Ground Fault - TCC - Multiple of sensor 1

Status
Not open for further replies.
Replies continue below

Recommended for you

The shape of the curve doesn't change. Just slide it from 0.8 to whatever pickup setting you want, noting that the actual pickup band is above the nominal setting. Also, the actual range of pickup settings for ground fault depends on the size of the breaker, due to NEC/UL. It can't be set higher than 1000 A primary. The time delay settings don't change.
 