Harry choi
This is choi from Korea. I’m electrical engineer.
Our client want to eliminate ground fault function in low voltage zone.
TR : 6.6/0.38kV
TR 2nd 3 phase short circuit current : 52kA
TR 2nd Line to ground fault current : 51kA calculated by etap.
Grounding system : TN-S
ACB and MCCB have trip device with long time, short time, and ground function.
I believe that there is difference between 3phase fault and ground fault when it comes to equivalent circuit.
But our client claims that high ground fault current can be protected by ACB and MCCB’s phase protection.
It seems to be reasonable because CB will operate when high current of only 1 phase.
I don’t want to eliminate ground fault function. So I’m looking for IEEE or IEC stanrd.
Is there any reason to maintain OCGR function?