alex444
Electrical
- Apr 13, 2001
- 9
Hiya all,
I experienced a ground fault trip when energizing a 1500 kVA transformer during a system startup and would like some input/comments from you all.
The electrical distribution system is a 4160V, 3 phase, 4-wire, solidly grounded system. The feeder breaker load is a 1500 kVA delta-wye transformer.
The breaker protective relay is a Cutler-Hammer Digitrip 3000 with the following ground fault settings:
CT pri: 200
LTPU: .1x
Curve: FLAT
Multiplier: .2s
The transformer load consisted of both 3 and single phase loads connected to it and that would start on energizing.
On energizing the transformer it tripped out on GF. I raised to the next setting which was .25s. It still tripped. Raised the setting to .3s and it held.
When it tripped out on GF, the trip unit recorded 40-50 amps. On the .3s settings, it read 0 amps.
My question is: Why did I have nuisance trips?
I looked in the IEEE Buff book but it skims overs nuisance tripping in the section for Ground Fault Protection.
If it tripped due to load imbalance, inrush, or CT mismatching due to tolerances, it should have held at .25s since there was more than enough time (cycle wise) for the transformer to settle.
Any help/comments are welcome.
I experienced a ground fault trip when energizing a 1500 kVA transformer during a system startup and would like some input/comments from you all.
The electrical distribution system is a 4160V, 3 phase, 4-wire, solidly grounded system. The feeder breaker load is a 1500 kVA delta-wye transformer.
The breaker protective relay is a Cutler-Hammer Digitrip 3000 with the following ground fault settings:
CT pri: 200
LTPU: .1x
Curve: FLAT
Multiplier: .2s
The transformer load consisted of both 3 and single phase loads connected to it and that would start on energizing.
On energizing the transformer it tripped out on GF. I raised to the next setting which was .25s. It still tripped. Raised the setting to .3s and it held.
When it tripped out on GF, the trip unit recorded 40-50 amps. On the .3s settings, it read 0 amps.
My question is: Why did I have nuisance trips?
I looked in the IEEE Buff book but it skims overs nuisance tripping in the section for Ground Fault Protection.
If it tripped due to load imbalance, inrush, or CT mismatching due to tolerances, it should have held at .25s since there was more than enough time (cycle wise) for the transformer to settle.
Any help/comments are welcome.