HeinzM
Electrical
- Jul 13, 2017
- 9
Is anyone able to give me a clear explanation of fault current flow on the attached 1-line with fault locations in case 1 and 2?
The incoming utility service is a 13.2 kV delta. The 480V generator is connected with a 13.2 kV wye-gnd to 480 V delta transformer.
On a recent utility fault on the incoming service, breaker 52F1 (gen-bus) tripped on ground fault and locked out the gen from islanding.
We want to change protective relays, to selectively trip 52F1 or 52U, depending on the fault location.
The incoming utility service is a 13.2 kV delta. The 480V generator is connected with a 13.2 kV wye-gnd to 480 V delta transformer.
On a recent utility fault on the incoming service, breaker 52F1 (gen-bus) tripped on ground fault and locked out the gen from islanding.
We want to change protective relays, to selectively trip 52F1 or 52U, depending on the fault location.