Is there a standard or common practice for installing new grounding systems for new unit substations or electrical rooms that reside within an industrial facilities distribution system. An example would be an elevated electrical room (IPA building) which is supported by a foundation and contains MV & LV switchgear as part of a unit substation with transformers located outside of building.
From what I have seen most electrical room or E-Houses of this nature in an industrial facility typically have a ground ring which surrounds the building with rods at each corner and is also tied into the rebar in the building foundation (UFER Ground).
To me a ground ring designed per IEEE 80 is more reserved for a MV/HV outdoor substation with a large footprint which will be more susceptible to step and touch potentials.
Does anyone have any good guidance on when to install a ground grid per IEEE 80 vs a ground ring as described above?
From what I have seen most electrical room or E-Houses of this nature in an industrial facility typically have a ground ring which surrounds the building with rods at each corner and is also tied into the rebar in the building foundation (UFER Ground).
To me a ground ring designed per IEEE 80 is more reserved for a MV/HV outdoor substation with a large footprint which will be more susceptible to step and touch potentials.
Does anyone have any good guidance on when to install a ground grid per IEEE 80 vs a ground ring as described above?