rwilsond

Electrical
Aug 24, 2005
21
A large 1 MVA, Delta-Wye transformer supplies a 480V, 3-Wire MCC via a bus-duct. The 20-foot length of bus-duct contains NO ground-bus, and no neutral, and the enclosure is NOT Listed for grounding.

The transformer secondary, and the Ground-Bar inside the MCC, are both connected to the grounding electrode system (i.e., underground ground grid, etc.).

Where in the NEC is this prohibited?
 
Replies continue below

Recommended for you

See 250.4(A) if XO is grounded or 250.4(B) if XO is floated.
Don
 