GROUND PLATE INSTEAD GROUND ROD

Status
Not open for further replies.

pristava

Industrial
Jan 8, 2004
53
Communication Antenna is provided to be grounded with three
ground rods ( 3.0 m long) connected by 2/0 wires. Also connection with existing grounding is provided to be made.
Contractor is preparing to intall three ground plates instead ground rods.
Question:
How to calculate grounding in that case ? Is it possible to replace ground rod by ground plate making the same grounding resistance.
Thanks!
 
Replies continue below

Recommended for you

I don't have access to it here to check, but the IEEE Green Book has ground impedance calculations for many different configurations of ground equipment.
 
Specify the resistance you need to the contractor then let him do the math.
 
Resistance to earth can be calculated roughly if soil resistivity is known. Sometimes it is necessary to use trial and error approach (e.g. start with 2 or 3 and add more as needed to get desired result).
 
Suggestion: The lightning protection should be grounded according to up to date 2000 edition of:
NFPA-780 Standard for the Installation of Lightning Protection Systems (1997)
The antenna system grounding is specified under the transmitter/receiver spec.
See NFPA 70-2002 National Electrical Code for Article 810 Radio and Television Equipment. (There is no specific Ohms value stated for the antenna grounding.)
 