nchrista
Electrical
- Mar 15, 2005
- 18
Hello All,
I created a ground grid for a multi-peaker unit site with soil resistivity in the neibhborhood of 10.7 ohm*m. There is approximately 7000 meters of 4/0 copper with some 500 kcmil in the heavy fault (60kA) area. The grid area is in the neighborhood of 300km^2. My calculated GPR is around 550V and my touch potential for a 0.5 second clearing time and a 50 kg person is around 50V. The calculated worst case touch potential is around 410V. Should the 410V value be greater than the GPR?
Can someone tell me whether I am reading this correctly?
My concept of the grounding calculation was that as long as the touch potential is greater than the GPR then we were covered. But after adding more ground and stiffening the grid altogether the touch potential has gone down substantially whereas the GPR has only gone down a fraction of a percent.
I created a ground grid for a multi-peaker unit site with soil resistivity in the neibhborhood of 10.7 ohm*m. There is approximately 7000 meters of 4/0 copper with some 500 kcmil in the heavy fault (60kA) area. The grid area is in the neighborhood of 300km^2. My calculated GPR is around 550V and my touch potential for a 0.5 second clearing time and a 50 kg person is around 50V. The calculated worst case touch potential is around 410V. Should the 410V value be greater than the GPR?
Can someone tell me whether I am reading this correctly?
My concept of the grounding calculation was that as long as the touch potential is greater than the GPR then we were covered. But after adding more ground and stiffening the grid altogether the touch potential has gone down substantially whereas the GPR has only gone down a fraction of a percent.