One my engineers design a valve control house. This buildign has three rooms: the lectrical room the generator room and the valve control room. The electrical service is at 2400 volt, 3 phase, 3 wire wih a 45 kVA transformer and we install a pad monted transfromer inside the electrical room to lower the voltage to 480/277 volts. We design a ground grid with 6 ground rods around the building and in the technical specifications we indcated that we want 5 ohms of ground resistance. We also indicated that all equipment shall be grounded and we brought a ground conductor for every single equipment. We did not measure the soil resistivity during the design so we did not know if we were going to get 5 ohms with this 6 ground rods, but we indicated that the contractor shall add additional ground rods to get the 5 ohms.
Well, during construction the contractor measure the ground system and got 14 ohms. He added 7 additional ground rods and was able to get to 11.5 ohms. At this time he indicated that to get to 5 ohms is not reasonable since the contract is defective. The soil at this location is granite and we did not know until we got there.
At this time we though that will be sufficient and we are thinking to accept it as is.
The client indicated that since the contract requires to have 5 ohms it should be forced to the contractor to obtain 5 ohms.
There are several issuses in here:
1st. Is it necessary to get to 5 ohms of ground resistance? why?
2. I understand that we can use special ground rod and get to the 5 ohms, but the issue is what are we really gaining?
I read the IEEE 80, 141, 142, Soares bbook on grounding, the NEC, OSHA grounding requirments and nobody says the reason why we need to get to 1 ohms, or 5 ohms or less than 25 ohms. I would like to know if somebody can explain the need to get to 5 ohms or very low ohms in general.
Is the cleint right to force the contractor to get to 5 ohms or is it the engineer's at fault and paid for the extra effort to get to 5 ohms?
Well, during construction the contractor measure the ground system and got 14 ohms. He added 7 additional ground rods and was able to get to 11.5 ohms. At this time he indicated that to get to 5 ohms is not reasonable since the contract is defective. The soil at this location is granite and we did not know until we got there.
At this time we though that will be sufficient and we are thinking to accept it as is.
The client indicated that since the contract requires to have 5 ohms it should be forced to the contractor to obtain 5 ohms.
There are several issuses in here:
1st. Is it necessary to get to 5 ohms of ground resistance? why?
2. I understand that we can use special ground rod and get to the 5 ohms, but the issue is what are we really gaining?
I read the IEEE 80, 141, 142, Soares bbook on grounding, the NEC, OSHA grounding requirments and nobody says the reason why we need to get to 1 ohms, or 5 ohms or less than 25 ohms. I would like to know if somebody can explain the need to get to 5 ohms or very low ohms in general.
Is the cleint right to force the contractor to get to 5 ohms or is it the engineer's at fault and paid for the extra effort to get to 5 ohms?